julesmoto said..MysticCastle said..julesmoto said..So I have built a support structure to support two house size 330 watt 24 volt panels (arriving tomorrow) which will double as a Bimini. I have three batteries on board one of which which is a fair way from the panel up the front of the boat to power the anchor winch. All 3 lead acid batteries are different brands and ages. Thinking of charging the two rear ones of one panel and the front one of the other panel via 3 different cheapy charge controllers as I don't want the charge controller to stop charging once the first battery gets to full charge.
2 questions.
Firstly is there any reason why I could not use the cheap charge controllers on eBay as follows which don't seem to have any heatsink capability but claim MPPT which I believe is necessary to go from a 24 volt panel to a 12-volt battery?
www.ebay.com.au/itm/284062092832Second question. How do I size the wire type and diameter which must travel about 11 m from the rear of the boat to near the front battery where I plan to put the third controller?
There is an existing cable that goes to that battery and it would be great if I could use the same one to avoid complex threading through bulkheads and cupboards etcetera. As this cable would now be at 24 volts from the solar panel presumably it doesn't need to be as thck as the existing one which hopefully is sized for 12 volts although I am considerably upsizing the size of the panel vs the old one (don't know what the alternator puts out but won't be using the engine enough to matter).
I would review the cheaper controllers on the basis of what input voltage they will accept. Yes MPPT operation will be also be suspect. Why voltage? My thinking is that (given the more distant location of the third battery) the solar panels in series (48 volt) running to a charge controller local to the remote battery might be an idea. The high voltage will mean lower current over this cable run and thus keep the wire gauge down. But again - the cheaper controllers may not "like" the voltage from panels in series and MPPT WILL be required. In addition non house grade solar panels are labelled not to be run in series . . . but this is not likely for house grade panels as they are run in series on a house roof. Local to the existing twin batteries you can use a second charge controller and a smart FET based switch to switch the charge from one to both batteries when the first is charged but in this case it is better for both batteries to be similar in age and capacity - maybe a third controller is the option as you suggest above - then the battery technology / capacity / age will not matter for any of the batteries. I would also recommend in all cases a charge controller with Lithium (LIFEPO) charging support - future proof the investment in the controller/s.
Thank you for this reply and all the others that people have given. Excuse my ignorance but what is an FET switch? I am kind of back to square one now because the cheap solar controllers that I ordered three of, one for each battery, turned out not to be MPPT at all despite being advertised on eBay as such. Obviously they are going back. After that experience I think I will go with Renogy or Victron at considerably more expense. When the controller is rated at a certain amperage does this mean the amperage between the solar panel and the controller or the panel and the battery? The theoretical maximum amperage is of course double between the panel and the battery as compared to the panel to controller when the battery bank is 12 volts and the panel 24 volts. Presumably however the controller knows this and as long as it is not fed in excess of it's maximum rating it knows not to exceed this rating when dishing out to the battery??
Also presumably no matter how good the controller is it can't distinguish between two different parallel connected batteries at different states of charge??
I should have been more explicit re FET switch. I referred to a means to auto isolate a start battery from the house battery. ie when the charge voltage is high the start battery is connected (for charging) and when the charge voltage drops below a threshold the start battery is isolated from the house wiring. A relay based switch can do this also.
I referred to running the panels is series to avoid heavy wire gauge going forward almost the full boat length to the winch battery - but only if there is a MPPT solar controller co-located with the winch battery. As mentioned above, ohms law kicks in. Two panels in series is approx 48volt. The current will be the same as the max current from one panel. (test by short-circuit of the panel with an appropriately rated meter). Two panels in parallel will be 24 volt and double the current than the series option - fatter wire required.
This approach does NOT work for a PCM controller - the higher voltage is wasted and not "converted" to changing power.
A true MPPT (Multi Point Power Tracking) controller will adjust the load the panels see to achieve maximum power output from the panels. The power (volts and current) required to be delivered to the battery is kind of decoupled from this - what does happen is that as the power needed to be delivered to the battery is measured, the new MPPT point of the panels is computed. So while getting the max out of the solar panels, the MPPT controller gets the best charge into the battery.
On Victron - yes a good choice but please note that if you go lithium in the future the documentation does NOT state in a very clear manner how to upgrade Victron controllers to run lithium batteries - they can be - even though the sales gumph does not mention Lithium - and I find this very strange. If you get a Bluetooth capable Victron then you can update later. If you do not get bluetooth - cheaper option today - then you will have to return it to the place of purchase (edit for re-programming) or buy the blue tooth adapter.
You can also look at iTechworld in WA. They sell a MPPT controller that is rated for 30A and up to 100volt input from the panels. I am using it on a LIFEPO house battery at present.
The options I see are:
Series or parallel or independent panels
- series means one wire run from the panels and wire sized in current rating for the short circuit rating of one panel
- parallel means double the current from the panels so either an increase in wire thickness from panels to the controller OR run the panel wires separately from the panels and place in parallel AT the controller. ie same as series wire gauge just double the wire length.
- independent means separate wires runs from each panel to separate house and winch controllers. The longer run to the winch controller will have to have increased wire thickness.
One or two or three MPPT controllers
- one, then all batteries should be the same and placed in parallel
- two, separate winch controller located in the bow and should be run from a series panel arrangement to reduce the wire size from the panel. This battery can be optimised for the winch operation now (high current). The run from the winch battery to the winch is short.
- three, overkill IMO - the cost of a third controller is better spent on matching the house batteries?
Personally I would build the two controller option with series panels. This allows lower rated wiring from the panels to the controllers (half the current of a parallel option), allows the winch battery to be sized independently to suit the heavy current required, the house batteries should be in parallel and thus be the same but do not need the heavy discharge current capability opening up other options aka Lithium in the future. I would take particular care to differentiate the >48volt wiring of the series panels however.