Hi Dralyagmas
I was hoping that someone where may have come across these pressure switches and how to set it.
That's me, I suppose.
What you have here is a duel pressure control switch.
On the lest side is the
high pressure cut out switch.This is to protect your compressor from a high pressure situation and is factory set for your system and
should not be altered.What is a high pressure situation.?In an air cooled condenser, the fan draws air through the condenser coil , cools the gas which condenses into a liquid and also draws air across the compressor which keeps it a little cooler.
If the fan stops,the gas pressure will rise higher than the compressor can handle. This will lead to a high amperage draw, a hot compressor and eventually compressor failure.
If the condenser is blocked buy a stray plastic bag or other obstruction, the gas pressure will rise higher than the compressor can handle. This will lead to a high amperage draw, a hot compressor and eventually compressor failure.
If there is a leak of refrigerant,, air will be sucked into the system,the gas pressure will rise higher than the compressor can handle. This will lead to a high amperage draw, a hot compressor and eventually compressor failure.
In the case of a water cooled condenser high pressure would be caused by pump failure, partial or complete blockage of cooling water or air in the system as per above.
The right side is a
low pressure control switch.This is to protect the system if there is a refrigerant leak and to control the refrigerant flow to allow a low amperage draw start up.
Again this is factory set for your system and
should not be altered.The only time that this is altered by a technician is when the type of refrigerant is changed (i.e, the system ran on the old type of refrigerant, and is recharged with the new generation refrigerant).
The cut in/ cut out of your compressor is controlled by the thermostat in conjunction with the low pressure control.
In most (light duty) systems the thermostat cuts out at the set temperature and after the temperature in the cooled space rises a preset level (temperature difference = T.D.) it cuts back in again. The T.D is usually preset.
The location of the thermostat sensor (bulb) is important. If it is close to the cooling plate (evaporator) it will sense that low temperature and not the actual air temperature inside the cooled space.
If it is too far from the evaporator.it can lead to the evaporator freezing up and losing efficiency.
In your system with a dual pressure controller,
I suspect the thermostat will open when it reaches the set temperature.
The open circuit
will close a solenoid valve and stop the refrigerant flow.
The compressor will continue to run until it lowers the pressure to the preset level on the low pressure control switch and the compressor will cut out.
In this situation the pressure on the inlet (suction) and outlet side (discharged are almost balanced).
The thermostat will close after the cooled space temperature rises to the T.D., the solenoid open, the gas flows and the compressor will start in response to the setting on the low pressure control switch.

Solenoid valves
So. adjusting this will do nothing to getting your refrigerator operating at a lower temperature.
The 2 eutetic plates are at the back of the compartments and the difference between each compartment is just the refrigerant type. The system has only 1 control for both with changes in this effecting changes in both the fridge and freezer.
In my view 2 evaporators means two thermostats and two solenoids. If you are getting 3 degrees from you fridge that should be fine.
Ideally minus 15 is good for your freezer. Best setting are 1 degree and minus 17.
First question is has it always been like this or have you noticed a deterioration in cooling?
Check what temperature your thermostat is set at.
If you set it lower the system will run longer.
You can look for your freezer thermostat sensor and experiment with positioning it.
Another shot could be short of gas. If you have a sight glass in the system there should be no bubbles in normal running conditions. Some bubbles at start up are normal.
Hope this helps
gary